Your GFCI at the house in GA is wired to a 15 amp breaker. So you are starting off with a power feed of only 15 amps. The distance you want to run will probaly not work on that size breaker. You can't put a 20 amp breaker on a GFCI. I would put a seperate run to the dock, or as close as the Corp. will alow, with 30 amp breaker and put the GFCI at the end of the run. you can also get a GFCI breaker for the end of the run.
The twist lock cord end is for safety. Keep it.
Ok, now I'm worried, I checked the panels and my GFI circuits all have 20a breakers.... Going to double check.
Last night at Lowes I did find standard extension cord plugs that had a twisting waterproof connector. I think that may be my best option since the existing plug is a locking connector, but doesn't have a waterproof enclosure.
***Edit / Update***
The GFI circuits are 20a. I have 15a Arc Fault breakers too, but those are for the bedrooms.